Cable capacity reduction due to harmonics

Cable capacity reduction due to harmonics

Cable capacity reduction due to harmonics

(OP)
Hello,
We have a cable installation (separate conductors) feeding a VFD - 5.5 MVA. Converter is "6-pulse" type.
The feeding cables will run 98% full load (24-7), and we are not sure if the cable capacity should be upgraded due to the harmonics. Right now we have not the exact numbers for THD and frequency content, but can anyone give us general design hints and common practices. Also litterature recommendations are highly appreciated.
Best Regards
Petersen

RE: Cable capacity reduction due to harmonics

I have a paper by D Rice (IEEE Transations on Industry Applications, Jan 1986 - "Adjustable Speed Drive and Power Rectifier Harmonics - Their Effects on Power System Components" that calculates a derating factor based on the assumption there is NO resonance, a 6 pulse waveform, and ignoring the proximity effects of surrounding conduit, armour, etc. It is based on HLF (Harmonic Loading Factor) which is the ratio of harmonic current fundamantal current / cable rated 60 Hz current. As an example, a graph is shown that indicates that with an HDF  of 100%, a 1000 MCM would need to be derated to 94%. This is the worst case on the provided graph.

If you can get hold of a text by G. Anders on Cable Rating, I think you will find more detailed methods that account for some of the assumptions mentioned above.

RE: Cable capacity reduction due to harmonics

When you say the cable is 98% full load what do you mean?
Is that 98% of the actual capacity? I hope not.

RE: Cable capacity reduction due to harmonics

(OP)
Thanks for your tips on papers.

And yes, the current in the cables will be 98% of the rated cable capacity (if we do not change the cables).

wereagle "hope not" why?

RE: Cable capacity reduction due to harmonics

JP
You post "The feeding cables will run 98% full load (24-7)"
is the reason I asked the question. I may not understand you situation correctly but the NEC requires cable to have an ampacity of 125% of the continuous load which makes the cable 80% loaded.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources