multi-thermostate in one zone
multi-thermostate in one zone
(OP)
hi;
Is it practically accepted to use multiThermostate in the same zone has multi-units.
thanks.
Is it practically accepted to use multiThermostate in the same zone has multi-units.
thanks.





RE: multi-thermostate in one zone
You could have one thermostat control multiple units where possible.
RE: multi-thermostate in one zone
RE: multi-thermostate in one zone
If you are fortunate enough to have a DDC system with some horsepower, you could write a quick and dirty routine to prevent a new mode from being entered unless all units were in vent only mode.
Lacking a DDC system if your units use sensors instead of contact closure stats, you could wire the stats in a series parallel configuration. This would have all units see the average temperature of the space.
If you have thermostats you could use relays to prevent zone contention.
RE: multi-thermostate in one zone