hi;
Is it practically accepted to use multiThermostate in the same zone has multi-units.

thanks.

RE: multi-thermostate in one zone

Multiple thermostats can cause problems in the same zone, depending on their proximity, they may tend to fight each other.  One thermostat may be affected by the device controlled by a separate thermostat.  

You could have one thermostat control multiple units where possible.

RE: multi-thermostate in one zone

If you have a DDC system you can use multiple thermostats and control all the units based on the worst case/average temperature in the zone.

RE: multi-thermostate in one zone

What you need to watch out for is contention or fighting between thermostats.  In a large zone with multiple units I have seen one unit heating and one unit cooling.  Obviously this is not the most energy efficient way of conditioning the space.

If you are fortunate enough to have a DDC system with some horsepower, you could write a quick and dirty routine to prevent a new mode from being entered unless all units were in vent only mode.

Lacking a DDC system if your units use sensors instead of contact closure stats, you could wire the stats in a series parallel configuration.  This would have all units see the average temperature of the space.

If you have thermostats you could use relays to prevent zone contention.

RE: multi-thermostate in one zone

If you have zoned your buildings A/C correctly so that the multiple units are all serving a similiar zone ie all units provide heating and cooling to west perimeter zone, and taken that the different areas within this zone have similiar internal loads and usage, similiar outside air proportions and  occupant / lighting and equipment densities. Multiple thermostats in the same zone will not cause a problem as all units provide for common or same building load profiles.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources