Air Cooled Chiller / Roof Top HVAC Unit not used for two years

Air Cooled Chiller / Roof Top HVAC Unit not used for two years

Air Cooled Chiller / Roof Top HVAC Unit not used for two years

(OP)
Hi,

Have a building, that was not used for more than two years. Now the client wants to use it again after some renovations.

Are there some procedures / checklist to be followed to check the systems before start up ??
I am contacting the vendor (carrier) …but if some of you have similar experience …it would help.

Thanks

RE: Air Cooled Chiller / Roof Top HVAC Unit not used for two years

1. Totally remove the refrigerant. Flush the refrigerant circuit. Vacuum it and remove moisture. Better if you replace the refrigerant.
2. Replace oil.
3. Clean suction and discharge valves of the compressor.
4. Clean liquid line filter.
5. Grease fan bearings.
6. Better if you clean the air side of condenser.
7. Check crankcase heater.

Regards,



RE: Air Cooled Chiller / Roof Top HVAC Unit not used for two years

Have Carrier sample the refrigerant first instead of just purging it out. Replace all filters. Clean all coils. Check fan bearings. Clean out condensate drain piping. Remove all loose rust and prime paint. Make sure you inspect the units. Check condition of all insulation, fan belts, bearings, vibration isolation. Have Carrier check out controls. Have balancing contractor balance air flows and set minimum OA CFM.

RE: Air Cooled Chiller / Roof Top HVAC Unit not used for two years

ALSO HAVE ALL SAFETIES CHECKED OUT.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources