Dear members,
I would appreciate your help in this matter.  DC ground fault keeps coming in and out (stays for a second then dissapears).  Any troubleshooting ideas??  Loads off the DC bus cannot be isolated due to their criticality.

What is causing for fault to cycle rather than stay on the system?  Thanks.

RE: dc ground fault on battery charger

ZZap,

Welcome to the world of ungrounded systems!

Possible reasons why the ground fault alarm comes in and out: the fault is resistive, and the threshold is on the margin for the monitoring relay; the fault is related to local ambient conditions, such as rain, steam, sun if you are lucky enough to see it this time of year, etc.

What are loads on the system? If they are, say, field-mounted instruments on switchgear or transformers, this kind of fault is not uncommon.

There are some interesting instruments which can detect and locate ground faults. The one we use is called a 'Grouser' (not 'growler', which is a toy that the motor repair guys use). The instrument works by injecting a fairly small low frequency AC current into the loop formed by the faulted pole of the DC system and the earth. A sensitive detector using a coil on a ferrite core traces the injected current along the core to the location of the fault. It can be a laborious process, especially if the fault is at an awkward location such as the top of a power transformer.

Prior to buying the Grouser, we constructed a similar arrangement using a signal generator, power amplifier, and a coupling transformer. The arrangement worked well until the day when someone cranked up the 600W power amp somewhat while tracing a high-resistance fault, and knocked out part of the 11kV network by operating one of the protection relays. Ooops! Moral: be careful if the loads are critical.

This link shows the instrument, about halfway down the page. I can't find the manufacturer's website at present.

http://www.groupcbs.org/T&Mequipments.htm


----------------------------------

If we learn from our mistakes,
I'm getting a great education!

RE: dc ground fault on battery charger

You may want to consider the BENDER EDS3365 Portable Ground Fault Locator for ungrounded AC and DC systems.  Many utilities are using it to detect ground faults in their 125/250V DC systems.  Information is available at www.groundfault.com under the products section.

RE: dc ground fault on battery charger

One thing that has worked for me is vacuuming out the dust that had accumulated in the charger.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources