Cable experts guidence please ....
Cable experts guidence please ....
(OP)
One of the cable manufacturers catalogue specification says 3C,Cu?XLPE/SC/Cu-tape screen/SWA/PVC rated 18/30kV(36kV) manufactured as per IEC-60502.Can i use this cable for 34.5kV rated system. What does their specified 18/30kV rating means? What does the above IEC standard says? Can some experts brief me in details?





RE: Cable experts guidence please ....
The first bit describes the construction:
3C = 3 conductors
Cu = copper conductor
? = not sure, but it should be a semi-conducting layer
XLPE = crosslinked polyethylene
SC = semi-conducting screen
Cu-tape screen = copper tape screen ;-|
SWA = steel wire armour
PVC = polyvinyl chloride overall jacket
10/30(36) kV = 10 kV phase to ground, 30 kV phase to phase, 36 kV maximum system phase to phase.
For use in a 34.5 kV system, I can't say for sure, but I suspect 'no' because the cable is rated at only 30 kV l-l.
The IEC standard is lengthy. You can buy it at www.iec.ch.
RE: Cable experts guidence please ....
I understand why you posted this in two fora, but please try to minimise it - imagine the mess if everyone double posted! Many of us who read the electrical power forum also read this one, so you would get you answer.
----------------------------------
If we learn from our mistakes,
I'm getting a great education!