Live and dead loads surcharge for tieback block retaining walls
For the design of segmental block (tieback) retaining walls, specifically for the Rockwood Classic 8 wall system, are there typical design values for live load and dead load surcharge that are generally used for site projects? For example, I have seen several examples that seem to use 100 psf for a parking lot surcharge, and 250 psf for a building surcharge. If there are accepted design values, where can I find them? Thanks.
RE: Live and dead loads surcharge for tieback block retaining walls
In highway design, the minimum traffic surcharge per AASHTO is equal to 2 feet of dirt surcharge or 250 psf (vertical) minimum. Can trucks (e.g., moving trucks, fire trucks, delivery trucks, etc.) get to the back of the proposed wall?
Am I correct in assuming that these surcharge loads should be considered if the loads are applied inside the soil failure plane? For example, in the case of a slab foundation, should I apply the portion of the slab that is transmitting the load inside the failure plane?