Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login




Remember Me
Forgot Password?
Join Us!

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.
Jobs from Indeed

Link To This Forum!

Partner Button
Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

7carisfast (Electrical) (OP)
8 Dec 04 10:30
Look for some advice on adding secondary GF protection on a 4000KVA 13.8/4.16KV transformer.  Does anyone have a link which explains my options or can anyone give some advice?
busbar (Electrical)
8 Dec 04 16:12
 
What is the 4kV system-grounding method—ungrounded/solid/high-resistance/low-resistance?

Start with IEEE Std 142 §1.
  
PWR (Electrical)
8 Dec 04 17:11
A 4.16kV delta transformer connection offers no neutral point on which to establish a solid, low, or high resistance ground connection.  Is it your intent to operate ungrounded(rarely practical at 4.16kV) or do you wish to utilize a zig-zag grounding transformer to establish a neutral?  What type of loads do you have?
7carisfast (Electrical) (OP)
9 Dec 04 9:06
The method is an ungrounded 4.16KV Delta.  The loads are all motors.
dpc (Electrical)
9 Dec 04 12:41
The most commonly used ground detection scheme involves three voltage transformers connected grounded wye -  broken delta.  One corner of the secondary delta is left open and a voltage relay is connected across the open corner (along with a resistor to prevent ferro-resonance.)

The voltage across the corner will be 3Vo.  

See any relaying text, such as Blackburn's "Protective Relaying".  

PWR (Electrical)
9 Dec 04 14:18
Based on industrial practice in the US, you are fighting history to operate motors at 4.16kV ungrounded.  I can cite plants that "gave up" trying to operate such systems in the 1950s and 60s.  Since then, more, not fewer problems have been identified with ungrounded systems. I'm not saying it can't be done, but the question is why?
busbar (Electrical)
9 Dec 04 16:37

To add to dpc’s comments, the transformer primaries, although normally exposed to ø-n voltage, must be rated for full ø-ø voltage—id est, 35:1 [not 20:1] for this application.   

Chapter 6 of Beeman’s IPSH (circa 1955) has a very lucid description of the potential problem.  It is very real—with tragically expensive results at 480/600V, murder at 4160V, and mass suicide at 12kV.
   
dpc (Electrical)
9 Dec 04 16:42
I used to think this type of system had faded away in the US, but I am currently working on two system studies at east coast power plants that both have extensive 4160 V ungrounded systems, including a lot of big motors.  The plants have been operating this way for about 40 years.

So they are still around, in spite of the conventional wisdom that they are a problem.  
rbulsara (Electrical)
9 Dec 04 18:55
Look up 59G relay application. Best suited for ground fault detection on ungrounded systems (and high resistance grounded).

Here is one of the links..

http://www.byramlabs.com/pdf/basler/ubg7bull.pdf
busbar (Electrical)
9 Dec 04 19:27

If switchgear/motor/cable-run/transformer conditions have been kept consistently sanitary, and winding insulation has no 'weak spots,' it is possible for ungrounded systems to operate successfully, but practically, that is the exception to the general case.

Surge capacitors can be their own double-edged swords.
   
JoeBoardman (Electrical)
14 Dec 04 12:48
I would recommend using a Bender Ground Fault Monitor, e.g. IRDH275 with a voltage coupler, e.g. AGH520S.  It measures the resistance level of the ungrounded system and alarms when the resistance to ground drops below the alarm setpoint.  Also may want to look at RCM470DY Directional Ground Fault Relay too.  See http://www.groundfault.com.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close