Minium vertical distances between water, storm, sanitary

Minium vertical distances between water, storm, sanitary

Minium vertical distances between water, storm, sanitary

(OP)
I need some help with utility design.  I am a designer in Wisconsin and below are the guidelines I follow, but they are simply what I have been taught.  I have not been able to find a definitive code that defines these distances. My local code only lists minimum horizontal distances.  I

Water over sanitary = 6" between invert and crown
Water under sanitary = 18"
Water over/under storm = 6"
Sanitary over/under storm = 6"
Minium 6" cover over water

Any help would be appreciated.

RE: Minium vertical distances between water, storm, sanitary

(OP)
By the way, I meant to put 6' of cover over water, not 6"

RE: Minium vertical distances between water, storm, sanitary

Check the Standard State Specs

RE: Minium vertical distances between water, storm, sanitary

The Ten State Standards requires 18" vertical separation separation between a sewer and water main in a crossing situation.  Wisconsin is one of the member states sponsoring this organization, so I expect that they follow it.   Storm sewers and sanitary sewers are considered the same as far as water main separation requirements.  I don't know of any minimum separation requirements for storm and sanitary sewers.

Get a copy of Wisconsin's Standard Specifications for Water and Sewer Main Construction.   How have you been getting permits without knowing these requirements?

RE: Minium vertical distances between water, storm, sanitary

The separation has to be large enough to work on either or both pipes. Should always make the separation as much as practical both directions. I've had to repair sanitary sewers that had 5 feet of horizontal clearance with a 'parallel'storm drain.. Not a problem, until the storm drain edge was 6 inches into the edge of the sanitary line. It was hard to dig down 15 feet with that at the 10 ft. mark.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources