How we calculate the speed droop and voltage droop. if i have 6MW and 4 MW DG and have to run in ISland mode . wt will be the value
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Droop CAlculation
RE: Droop CAlculation
RE: Droop CAlculation
How do you propose to keep one generator in isochronous mode - i.e. at constant frequency irrespective of load - while another generator connected to the same system operates in droop mode - i.e. frequency drops as load increases - unless 'isochronous mode' on the larger set is not truly isochronous? It is not possible to have two generators running at different frequencies on the same bus.
Normally all machines on a common bus would operate in droop control to ensure load sharing, unless a more advanced controller is in use to provide constant output power control or PF control, or a supervisory controller designed to keep the prime mover or generator within thermal limits has over-ridden the other control loops.
----------------------------------
If we learn from our mistakes,
I'm getting a great education!
RE: Droop CAlculation
With steam turbines, the test can be performed from “HSS Speed, no load” to “ Speed, CVWO” by isolating the steam supply. For example, running 3852 rpms at HSS, the speed would decrease to 3672 rpms when the CV reach wide open, with 5% regulation. (3852-3672)/3600X100.
Some governors can have “isochronize” mode. This mode will sense there has been a “droop” and will automatically change “speed reference” to bring speed back to rated (with in a set amount of time) I think this may be "island mode". In which case, besides the regulation droop, there will be a time constaint setting. The very few isochronize control systems I have seen, the regulation was set in "grid mode" and the time constaint set in "island mode". They were electronic and calibrated with simuated speed.
Speed Regulation is a test that I routinely perform on turbine governors. Besides the regulation of load as frequency varies, it is important to verify that the governor will respond properly to prevent dangerous over speed in the event of a load rejection.