Droop CAlculation

Droop CAlculation

Droop CAlculation

(OP)
How we calculate the speed droop and voltage droop. if i have 6MW and 4 MW DG and have to run in ISland mode . wt will be the value

RE: Droop CAlculation

I believe if you look at your governor manual, there should be info on that.  Typically, for island mode the largest generator would be set for isochronous mode and the other generator set at 5% droop (which should be the normal setting).  

RE: Droop CAlculation

You don't calculate the droop, you set it according to what you want the response to be from no load to full load. Usually 4% is common, this will give you a 2 hz drop ie 50 to 48 on a 50 hZ system.

RE: Droop CAlculation

wbd,

How do you propose to keep one generator in isochronous mode - i.e. at constant frequency irrespective of load - while another generator connected to the same system operates in droop mode - i.e. frequency drops as load increases - unless 'isochronous mode' on the larger set is not truly isochronous? It is not possible to have two generators running at different frequencies on the same bus.

Normally all machines on a common bus would operate in droop control to ensure load sharing, unless a more advanced controller is in use to provide constant output power control or PF control, or a supervisory controller designed to keep the prime mover or generator within thermal limits has over-ridden the other control loops.

----------------------------------

If we learn from our mistakes,
I'm getting a great education!

RE: Droop CAlculation

Speed regulation testing used to be defined by ASME standards; I think IEEE is the current standard.  I am familiar with the procedures for steam turbines (ASME-PT20.X), but I would think those for diesel s would be the same concept.  The concept basically is, with the governor in “droop” mode operation, the “Speed Reference” is set to “Rated speed” at “Full load”.  Then, load is reduced and speed allowed increasing to the “No load speed”.  Regulation would be the percent change in speed from “rated speed full load” to “speed no load”.  For example, running 1800 rpms at full load, speed would increase to 1890 rpms at no load with 5% regulation.  (1890-1800)/1800X100.   

With steam turbines, the test can be performed from “HSS Speed, no load” to “ Speed, CVWO” by isolating the steam supply.  For example, running 3852 rpms at HSS, the speed would decrease to 3672 rpms when the CV reach wide open, with 5% regulation.  (3852-3672)/3600X100.   

Some governors can have “isochronize” mode.  This mode will sense there has been a “droop” and will automatically change “speed reference” to bring speed back to rated (with in a set amount of time)  I think this may be "island mode".  In which case, besides the regulation droop, there will be a time constaint setting.  The very few isochronize control systems I have seen, the regulation was set in "grid mode" and the time constaint set in "island mode".  They were electronic and calibrated with simuated speed.

Speed Regulation is a test that I routinely perform on turbine governors.  Besides the regulation of load as frequency varies, it is important to verify that the governor will respond properly to prevent dangerous over speed in the event of a load rejection.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources