two pumps in series with one vfd for one pump

two pumps in series with one vfd for one pump

two pumps in series with one vfd for one pump

(OP)
hi everybody,
can i use two pumps in series : one with constant speeed and the other with vfd?why?

RE: two pumps in series with one vfd for one pump

sure, but what do you want to accomplish is the more important question.....

RE: two pumps in series with one vfd for one pump

(OP)
it is a cooling tower pumps

RE: two pumps in series with one vfd for one pump

What it is mounted to is important but does not explain what you are trying to accomplish on that application. I think BobPE meant why do you want to vary the speed of one pump but not the other?

"Venditori de oleum-vipera non vigere excordis populi"


RE: two pumps in series with one vfd for one pump

Hi Naifmbo

yes this is done in certain circumstances, normally to avoid the cost of two VFDs but have some measure of flow control without throttling. It can make a lot of sense on a system where around 50% of the head is static lift and 50% is friction.
The normal area of debate is which pump should have the VFD. I tend to favour the first stage pump for ease of priming and less likelihood of accidentally producing a partial vacuum.

Cheers

Steve

RE: two pumps in series with one vfd for one pump

(OP)
hi every body,
i have already replaced my old 1 from 2 cooling tower pumps with pump has 20% higher head,so i want to keep this pump without trimming and install another pump with the same data and fvd.

thanks.

RE: two pumps in series with one vfd for one pump

If you are NOT planning to vary the pump speed for some process control benefits, it is not a good idea to use a VFD set for a continuous speed. The VFD is not 100% efficient so using it just to reduce to a fized speed will be at the cost of extra losses. If however you have something to gain by speed modulation to gain some additional control or savings then by all means do it.

"Venditori de oleum-vipera non vigere excordis populi"


RE: two pumps in series with one vfd for one pump

You can do it as you will be operating your pump at a constant speed with a VFD(huh...oxymoron).

Much cheaper options are,

1. Purchasing a new impeller
2. Controlling the discharge valve

Regards,

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources