This may be very basic for the expert members of this forum.On what basis do you select the short circuit withstand time on a switchgear (say HV switchgear)?
For example 40kA,1sec or 3sec ? Low voltage switchgears are generally found to have 3sec withstand time.
For example 40kA,1sec or 3sec ? Low voltage switchgears are generally found to have 3sec withstand time.






RE: Short circuit withstand time
The rated withstand time is always being used in conjunction with the rated short circuit withstand current.
Basically it is the max rms current a breaker (switchgear) can withstand without any damage (electrical, thermal, or mechanical damage or permanent deformation) linked to a certain time.
But, if you have to specify a certain withstand-time, you have to look how long a fault is going to stay on the system and how fast the protection is going to clear it.
Hope it answer your question.
Regards
Ralph
RE: Short circuit withstand time
Your withstand-time for a breaker must be longer than the time the protection is going to take to operate the breaker. (Under heavy fault condition)
Ralph