Use of series reactor for limiting the fault level
2

Use of series reactor for limiting the fault level

Use of series reactor for limiting the fault level

(OP)
Use of series reactors is one of the very common mode for fault level containment, but reactor can pose stability problem to the power system because it increases the over all reactance of the system. what do u say about the pros & cons of the reactor?

RE: Use of series reactor for limiting the fault level

Suggestion: The reactor manufacturers suggest reactor location within power distribution system where they are most effective with minimal impact on the system stability. Usual locations are in the power supply feeder(s), e.g. generator feeder(s), or utility feeder(s).  The main concern of in line reactors is the voltage drop rather then stability. If one can avoid them by proper design of generator and transformer impedances, one will have the better power distribution system.

RE: Use of series reactor for limiting the fault level

There was an article in the Doble Proceedings several years back about adding reactors on the neutrals of certain  transformers to reduce the maximum thru-fault that the transformer might be exposed to.  I think the author was Puget Sound Power.

RE: Use of series reactor for limiting the fault level

Suggestion: Visit
http://www.thomasregister.com
and type Reactors: Line/Load under Product or Service, which will return 12 companies to approach to

RE: Use of series reactor for limiting the fault level

I had an experience to use current limiting reactors with high impedance in the power distribution system of oil refinery complex. In conclusion, I decided to use fault current limiters instead of current limiting reactors, which cause voltage instability of power system.
When I conducted power system studies (Short Circuit Currents and Load Flow Studies), voltage profiles could not be maintained within the acceptable level due to high impedance of the reactors (it requires over 20% of impedance), and it did not allow satisfactory active power flows due to excessive reactive power losses.
Of course, it is no doubt that using CLR is a good option to reduce short circuit contribution, however CLR application shoud be carefully considered by conducting short circuit current calculaitons, load flow studies, etc.
In addition, I believe that main concern of CLR application is voltage dips under various operating conditions as already posted by "jbartos"

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources