Hi Forum,
I have a scenario. I have an equipment which can use dry feed and wet feed or both. When we use dry feed we use lots of water (400 l/s), when we use mixed feed or wet feed we use very less water (75 to 100 l/s). The flow is measured by an orifice plate (16" line size) and transmitter is calibrated for 0 to 500 l/s. The problem is, when we are on total dry feed transmitter is in 75% of the range which is desireable for good accuracy. But when we are on wet feed or mixed feed we are running it at around 75 to 100 l/s which is below 25% of the range and the accuracy goes to ...you know where. My question is, shall I install two flow meters? one for hi range and one for lower range or I can do something else? I do not want to change my orifice plate or modify my piping.
Thanks in advance for the responses.

RE: Dual ranges

Khan,

Two transmitters is a common way to deal with the problem of very large ranges. If the signals from the transmitters go in to a DCS or PLC, it would be a trivial matter to confgure a transfer block to select the high or low range transmitter depending upon the measured value. Include some hysteresis in the switching threshold.



----------------------------------

If we learn from our mistakes,
I'm getting a great education!

RE: Dual ranges

Khan101
Most types of flow meters (pitot, orfice, ultrasonic, propellor, turbine, disk) are accurate in a 10 to 1 turndown or less, the one exception is a Mag meter they are accurate at a 30 to 1 turndown.  The accuracy drops when the flow is less than 1 ft/sec (0.3m/sec) on most models.  the drawback is the cost (rough number $1000 per inch).  Replacement to a mag meter may be an option in your installation.  
Caution: mag meter do not work well with ultrapure waters (DI,RO)

Hydrae

RE: Dual ranges

A square-root relationship between flow and pressure differential applies to all head type meters.  Thus 70.7%flow is 50% dp, 50% flow is 25% dp, etc.  Head type meter turndown improvement is because the transmitter error is less significant now at 0.05% accuracy than 30 years ago when most transmitters had 0.5% accuracy.  The elements still may still have error from 0.5% to 2% of the full scale flow rate.  At 10% design flow the reading is quite low on the scale and error is high.  Do not plan better than 6:1 turndown from head type meters.

John

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources