Dual ranges
Dual ranges
(OP)
Hi Forum,
I have a scenario. I have an equipment which can use dry feed and wet feed or both. When we use dry feed we use lots of water (400 l/s), when we use mixed feed or wet feed we use very less water (75 to 100 l/s). The flow is measured by an orifice plate (16" line size) and transmitter is calibrated for 0 to 500 l/s. The problem is, when we are on total dry feed transmitter is in 75% of the range which is desireable for good accuracy. But when we are on wet feed or mixed feed we are running it at around 75 to 100 l/s which is below 25% of the range and the accuracy goes to ...you know where. My question is, shall I install two flow meters? one for hi range and one for lower range or I can do something else? I do not want to change my orifice plate or modify my piping.
Thanks in advance for the responses.
I have a scenario. I have an equipment which can use dry feed and wet feed or both. When we use dry feed we use lots of water (400 l/s), when we use mixed feed or wet feed we use very less water (75 to 100 l/s). The flow is measured by an orifice plate (16" line size) and transmitter is calibrated for 0 to 500 l/s. The problem is, when we are on total dry feed transmitter is in 75% of the range which is desireable for good accuracy. But when we are on wet feed or mixed feed we are running it at around 75 to 100 l/s which is below 25% of the range and the accuracy goes to ...you know where. My question is, shall I install two flow meters? one for hi range and one for lower range or I can do something else? I do not want to change my orifice plate or modify my piping.
Thanks in advance for the responses.





RE: Dual ranges
Two transmitters is a common way to deal with the problem of very large ranges. If the signals from the transmitters go in to a DCS or PLC, it would be a trivial matter to confgure a transfer block to select the high or low range transmitter depending upon the measured value. Include some hysteresis in the switching threshold.
----------------------------------
If we learn from our mistakes,
I'm getting a great education!
RE: Dual ranges
Most types of flow meters (pitot, orfice, ultrasonic, propellor, turbine, disk) are accurate in a 10 to 1 turndown or less, the one exception is a Mag meter they are accurate at a 30 to 1 turndown. The accuracy drops when the flow is less than 1 ft/sec (0.3m/sec) on most models. the drawback is the cost (rough number $1000 per inch). Replacement to a mag meter may be an option in your installation.
Caution: mag meter do not work well with ultrapure waters (DI,RO)
Hydrae
RE: Dual ranges