Average horsepower per cfm
Does anyone have a general formula for estimating horsepower (bhp) requirements per cfm?
I'm just looking for a rough number for estimating the fan motor horsepower on a large number of fan coils, and I would like to avoid selecting 150 fans at this point just to determine what the approximate bhp would be.
Any tips would be greatly appreciated.
RE: Average horsepower per cfm
bhp = (CFM x in. wg. total pressure)/(6344 x Efficiency in decimals)
For small fan coil units efficiency would probably be in the 0.40 to 0.50 range. Larger, more efficient units would be around 0.65. Check catalogs & solve for efficiency.
Total pressure would be external static + coil pressure drops + filter pressure drop.
Would it be right to say the factor in the denominator isn't 6344, but 6354 ?
25362,
Good point.  I think that factor is a function of air density, which can vary significantly depending on altitude and, to a lesser degree, temperature.  But either value works for a rough estimate.
ko  (www.ecooling.biz)