Is there a standard for Hazardous Location Static Grounding?

Is there a standard for Hazardous Location Static Grounding?

Is there a standard for Hazardous Location Static Grounding?

(OP)
I need a practical standard to refer to for grounding Static in a Hazardous Location.  Ideally something that suggests wire type, wire size, distance to objects, number of grounding rods etc.  NFPA77 has an appendix that has some pictures but no real recommendations.  My clients are looking for something more than “we like to see kind” of advise.

RE: Is there a standard for Hazardous Location Static Grounding?

I think your best bet is the Ammerican Petroleum Institutes (API) Recommended Practice RP 2003, Protection Against Ignitions Arising Out of Static, Lightning, and Stray Currents .
Another "introductory" would be APR RP 540 which covers general electrical installations.  It has a fairly comprehensive bibliography/reference section.

RE: Is there a standard for Hazardous Location Static Grounding?

(OP)
Thanks I've just down loaded the API document.  Its useful thank you.  I guess I'm looking for over simplified details. Everything I've read tells me that essentially every thing should be bonded and grounded but not how they should be bonded. I recognise that almost no current will flow on these conductors so wire size should not be an issue. On the other hand from a practical perspective I'm used to seeing a multi stranded #14 etc.  It would be nice to have a recipe book to refer to.

RE: Is there a standard for Hazardous Location Static Grounding?

Ah, well the "how" is generally covered in the National Electrical Code (NEC) Article 250, Part V, starting in section 250.90.  There are MANY options. The API 540 that I recommended also has a few details.  At this point, I'd also recommend the Process Industries Practices(PIP)at www.pip.org, but the “details” they have available for grounding/bonding are $1000.

My previous employer was a major contributor and I was a principal reviewer of many of the PIP standards.  I have since lost access to them though. They are still excellent and generally well accepted.  

RE: Is there a standard for Hazardous Location Static Grounding?

A good source of reference is Stewart R. Browne Manufacturing.  There publication "Grounding and Bonding Applications for Control of Static Electricity", is full of details, as well as parts lists and pricing.

RE: Is there a standard for Hazardous Location Static Grounding?

(OP)
Thanks this is exactly what I'm looking for.  I just whish it had the "stamp" of ANSI,UL, or NFPA etc.  Most other hazadrs have standards to which one can say you comply with.

Thanks again to rbalex. I doubt I'll be shelling out $1000 any time soon but the I have looked through the NEC it's not that diferent from what the Canadian code says. (The border never gets in the way of good practice). Thanks.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources