Cost to cool building?
There are obviously numerous assumptions to consider in what it would cost to cool an office building, but is there a general calculation to determine the cost of cooling an office building from one temperature to another using the square footage?
RE: Cost to cool building?
But that just gives demand cost for refrigeration. Then there's fan power that has pressure as a variable and there's no fixed relation between flow and operating cost. It's a function of duct design also.
We'd have to then add in water pumping with similar variables.
Each process or component would have to be adjusted for efficiency, then proportion all these requirements to load changes; mainly OA enthalpy.
There's maintenance costs, variable occupant loads and functions, etc.
I'd have to agree with Mint.
Best done by historical data - the US DOE has pretty decent book full of energy use data for different building regions/types/sizes.
OR, if there's an experienced building manager that's looked at this for his/her sampling of buildings - hopefully he/she would chime in...
Ton_hrs per year = (Kwh summer - Kwh winter)/(chiller kw/ton)
Full load hour per year = Ton_hrs / Total chiller tons installed
Estimated $ electric/year for cooling, pumps condenser fans but excluding $ for supply & return fan elect kwh = ($/kwh) x Total chiller tons x (Kw/ton chiller rating) x 1.2.
The factor 1.2 is based on about 0.1 kw/ton for condenser fans and 0.1 kw/ton for pumps.
Typical full load hours is 1000 to 2000 per year.