Can any one please explain the difference between the following CT accuracy classes?
5P10, 10B50 and 0.5M5
5P10, 10B50 and 0.5M5
Sarg
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
CT Accuracy: 5P10, 10B50 and 0.5M5
|
CT Accuracy: 5P10, 10B50 and 0.5M5CT Accuracy: 5P10, 10B50 and 0.5M5(OP)
Can any one please explain the difference between the following CT accuracy classes?
5P10, 10B50 and 0.5M5 Sarg Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
|
RE: CT Accuracy: 5P10, 10B50 and 0.5M5
M is designation for metering. 0.5M means that the CT max inaccuracy is 0.5%
Never seen or heared of 10B50.
RE: CT Accuracy: 5P10, 10B50 and 0.5M5
ANSI C57.13 is the relevant guide for instrument transformers.
There's a decent exerpt at the end of this document:
http://www.geindustrial.com/products/buyersguide/G...
RE: CT Accuracy: 5P10, 10B50 and 0.5M5
The CT accuracy class for 5P10 transformers per IEC Std 60185 is as follow: 5 = max. permissible total error, P= stand for protection and 10= Accuracy limit factor (ALF).
I am not familiar with the other two accuracy nomenclatures (10B50 and 0.5M5). However, the last one has appears to have some similarity with the nomenclature used in the Australian standard for CT’s.
If you should provide additional details such as project location, origin of CT, application, electrical parameter, manufacturer name or any relevant data, perhaps someone could help you.
In addition to the American instrument transformer standard, ANSI C.57.13, enclose are a few popular standards used for CT:
International/European: IEC 60044-1,
British: BS 3938 & BS 7626,
German: DIN VDE 0414-1,
Australian: AS 1675
Indian: IS 2705.
Japanese Standard