Cable size for Motors 1km away from controller
(OP)
I will install a 100HP 3Phase 60Hz 440V Induction Type motor 1 kilometer away from the Motor Control Center (Using Wye Delta starter). I'm planning to use 6 sets of 3x200mm sq Copper Wire. Is it sufficient, under or over design? Need your suggestions. Thanks
bold = bold
italics = italics
underline = underline
colored text[/color]
bold = bold
italics = italics
underline = underline
colored text[/color]





RE: Cable size for Motors 1km away from controller
Is this motor a submersible pump that is way down in a mine? An application that is that far away from the controller is almost always done using a 2,300 volt or 4,000 volt motor with an autotransformer reduced voltage starter or a medium voltage soft starter. A wye delta starter WILL NOT work 1 kilometer away from the motor.
Mike Cole, mc5w@earthlink.net
RE: Cable size for Motors 1km away from controller
The motor will be installed on a jetty 1000 meters away from the shoreline (location of the controller). The problem is, it was already purchased.
If the wye-delta starter is not possible, then we have to provide a power generating set near the motor.
Thanks a lot.
RE: Cable size for Motors 1km away from controller
What kind of load does this motor drive?
Are you locating the controller at the shoreline merely to save on service entrance equipment? If so, you are better off buying another fusible switch or circuit breaker and putting the controller at the motor.
Even if you try to brute force this with seven 1000 amp conductors ( 50% equipment ground plus 50% neutral because of the distance ) the cable capacitance will tend to cause the motor to act as an induction generator during the starting transition and during shut down. This could cause severe overvoltages when starting and stopping and also could create a large current spike when doing the wye delta transition. You may need rather hefty metal oxide varistor surge suppressors at both the motor and controller. You would need 12 at each end ( 6 phase to neutral and 3 across each winding and the other 3 across the wye contacts.
Also, in this application THWN conductors will have very high capacitance when wet. You will need to use XHHW ( cross linked polyethylene ) or EPDM conductor insulation because it will have less capacitance when wet.