Existing steel bad joist
I have a situating where mechanical engineers want to add an AC unit on existing roof. The roof construction is typical steel bar joist, metal deck, light weight concrete and water resisting membrane. Of course there is a suspended ceiling system. Nothing facny.
The building was designed in the late sixties. It appears that the structure was designed by an architect. The joists are spaced 6 foot on center with metal deck of unspecified height and three inches of concrete of unspecified density or type. This is of the plans sections and details.
It appears that the concrete is insulative type (I assume a weight of 2 PSF per inch of thickness). The deck, I assume is one inch high based on 6 foot span. The steel joists are 16H7. Using 20PSF live load and computing 14-PSF dead load I am able to determine that the joist load carrying capacity is almost maxed for its span. This is based on SJI’s load tables for 16H7.
I am able to locate the AC unit so that two sides will be bearing directly on steel beams that are well below their allowable stress and deflection. No problem.
I followed procedure that was published by Vulcarft in the 80 about designing joists for concentrated loads. Here is what I found:
1. The total moment capacity of 16H7 is above the new imposed uniform and concentrated load. From simple strength of material (shear and moment diagram)
2. The end reaction capacity of the joist seat is slightly above the actual reactions from the imposed uniform and concentrated loads.
3. When determining the uniform load on the joist using Vulcraft’s procedure, I came up with a “computed equivalent uniform load” that is about 10 pounds per foot larger that the joist allowable uniform load capacity.
I know that all the loads that I computed are based on full LL and DL combination acting simultaneously. How does everyone feel about the excess 10 pounds per foot?
I plan on calling Vulcraft and chatting with their engineers. Meanwhile, if you were in my shoes, what would you do?
RE: Existing steel bad joist
If you do decide you have an issue, I would consider strengthening the joists in place, since the joist seats appear to have capacity. I'm assuming the location is in Florida, and one problem I've noticed in Florida failures is the sudden load reversal causing internal joist weld failures (usually occurs at the first diagonal as it tries to punch past the bottom chord), then progressive failure of the joists (one that I checked about 10 years ago looked like it had been unzipped). When you have more DL+LL than was anticipated to begin with, you obviously have a tendency toward more deflection. When high winds (even the strong afternoon thunderstorm variety)hit, the uplift will pick it up and drop it suddenly. Not a lot of upward motion, but sometimes enough to pop a few welds.
Since this is 60's vintage, I doubt the joists were checked for uplift. You might want to run a check on the first diagonal for uplift and see if more bottom chord lateral bracing will be required (on all, not the ones you're looking at for the AC unit).
One other thing to consider is the moisture condition of the lightweight insulating concrete. In its equilibrium moisture content state (preferred), the moisture content will be around 10 percent by weight. This will yield a unit weight of about 25-28 pcf (about what you are estimating). Actual in-place moisture contents can range from about 20-25 percent to over a 100 percent. If you have a typical one, consider 30-50 percent moisture content (ask if they've ever had any roof leaks. The answer will be "yes", of course). With this moisture content, your unit weight will be about 33 to 38 pcf or more on the order of 3 or 4 lb/sf/inch.
I would first check that the location of maximum moment computed with the concentrated load is within the varying "envelope" of moment resistance of the joists, not just the maximum. The maximum allowable moment provided by the joist manufacturer at midspan is not necessarily true every where else in the joist (Which is why "KCS" type joists were developed.) Ditto for the shear strength of the joist. Its probably not uniform across the entire member.
Second I would be conservative in assuming what maximum live load that the joist might carry in addition to the new concentrated load. Is there a possibility of water collecting on the roof if a drain clogs? Is snow drifting an issue?
Third I would measure the joist chords and do an approximate check on the joists bending strength. Measure both the top and bottom chord cross sectional dimensions with a caliper after sanding off any primer. With a little research you can probably make a guesstimate of the lower bound of the possible yield strength of the steel from the 1960's. Calculations (examples of which are in SJI publications) will give you an approximate idea of what the joists maximum moment might be.
If after all this you find that the proposed loading is very close or just over your best estimate of the joists capacity, be conservative. Bite the bullet and carry the loads with new steel. Thats what I would do anyway.
Joists are typically fabricated very close to their reported maximum resistances, and the quality of welding and fabrication of joists isn't always uniformly good across every fabricator. So even if you're numbers say your ok, be conservative.
Its possible to augment an existing joist by welding on additional steel but this is not as simple as it might first sound (Some other posts in this forum dealt with this topic- try an advanced search to learn more.)
Good luck.
Did you notice I called it Bad not Bar Joist!! That is how I feel about touching these old buildings. Boy you never get the proper fee to doing them either.
Let me elaborate on items number 3. I calculated the maximum moment due to uniform and concentrated load. Then converted it to equivalent uniform load that would create the moment. I came up with 205 PLF that is well below the capacity of the joist of 269 PLF.
I calculated the new joist reaction due to the concentrated load. The new reaction is 4458 pounds. Joist seat reaction capacity is 4900 pounds. Which is good. However, I converted the maximum joist end reaction to equivalent uniform load that would generate this reaction and i cam up with 279 PLF. The 279 PLF exceeds the joist allowable uniform load capacity by 10 PLF.
I agree with your points. I am in Florida and uplift is a concern. I am not sure if the client wants to go and upgrade his roof structure to meet the uplift load reversal.
Thanks for you input.
"I am able to locate the AC unit so that two sides will be bearing directly on steel beams that are well below their allowable stress and deflection"
Why not design load transfer steel to carry all the weight on the steel beams?
1. The unit is rectangular.
2. There are two steel beams that are framing to a column and they are at 90 degrees of each other.
3. One beam is parallel with the joists and the other is supporting one end of the joists.
4. So envision that one of the short and one of the long sides are supported by the steel beam with the corner of the AC unit is directly at the column.
5. I am adding steel members between the joists to support the long and short sides of the AC unit.
The space for working in the joist is not impossible but not that easily accessible either.
Using your same process and THEIR maximum allowable end reactions, you get an equivalent uniform load of 306 lb/ft, which is greater than their stated 269 lb/ft. This would lead one to believe that they are working from empirical data, as is often done with bar joists. Using their same ratios, your equivalent uniform load would be more on the order of 225 lbs/ft which is well below their stated maximums.
Great forum. Many thanks for everyone who contributed.
For everyone's benefit, Vulcraft has a DOS program that is free to download at this link http://www.vulcraft.com/ and it is called VASSIST.
Based on my analysis and theirs, I am only 3.5% overstressed in shear. This is a small percentage and I can live with it.
Basically as long as my design moment, and end reactions do not exceed the allowable for the joist i am fine. Bending moment is below the allowable. Shear is 3.5% above the allowable and I am not going to lose any sleep over.
Well done forum, keep up the good work.
If you're going to use legs then it is still possible to support off of the two steel beams runninmg 90 degrees apart. Three of the legs would be directly over steel and the fourth could be supported off a a 45 degree piece of steel that spans between the steel beams and picks up the remaining leg.
It's your call, but it's a lot easier to put new steel on top of the roof rather than than on the inside.
Good idea. I need to see if there is room to install the diagonal beam and to ensure that the joist webs would not interfere.
I agree 100% on the roof penetrations. I have a detail with pitch pan or boot to go around the supports. Although I have not discussed in detail the actual support of the unit to the steel with our Mechanical engineers yet.
As always, this forum is great.
Have great day.