Strictly to test our control logic and our panel builds, we'd like to briefly run at no load several Baldor motors (7.5-20 hp) which are spec'd to be 380V/50 Hz. Our power supply is 480/60.
Given that there's no load and that we'd only be doing it for 60-90 seconds, is there any possibility of damaging the motors?
The vendor who quoted the system came back after we cut a PO for a duplicate system of one previously built and now says that they didn't quote dual-voltage motors on the new system and that if we want them then they have to increase the price. Of course, I don't want to pay any more than I need to.
Given that there's no load and that we'd only be doing it for 60-90 seconds, is there any possibility of damaging the motors?
The vendor who quoted the system came back after we cut a PO for a duplicate system of one previously built and now says that they didn't quote dual-voltage motors on the new system and that if we want them then they have to increase the price. Of course, I don't want to pay any more than I need to.
--------------------
Bring back the HP-15
www.hp15c.org
--------------------





RE: Dual Voltage Motors Needed?
Jeff
www.motors-direct.co.uk
RE: Dual Voltage Motors Needed?
An induction motor will have an equivalent magnetic load if the ratio Volt/Hertz is keep constant.
This motors are rated 380 Volts, 50 HZ so RatioV/HZ=380/50=7.6
The equivalent voltage at 60 HZ is; 7.6x60 = 456 Volts.
If your test is at 480 Volts the percent of overvoltage applied is; 480/456x100 =105.3%
Almost any standard for motor manufacture allows 5% overvoltage, NEMA allows up to 10% overvoltage.
RE: Dual Voltage Motors Needed?
Not so sure that I agree with that....would be very interested to know the results of your testing!!
Jeff
www.motors-direct.co.uk
RE: Dual Voltage Motors Needed?
"Venditori de oleum-vipera non vigere excordis populi"
RE: Dual Voltage Motors Needed?
RE: Dual Voltage Motors Needed?
This outfit is B$ting you about a higher price.
Mike Cole, mc5w@eathlink.net