hi ppl. can step and touch be measured or tested. Also after the earth grid in contructed can we measure its resistance?

RE: step and touch potential

see ANSI/IEEE std 81-1983 "IEEE Guide for Measuring Earth Resistivity, Ground Impedance and Earth Surface Potentials of a Ground System"

RE: step and touch potential

2
Ground resistance after construction is required by most utilities before the interconnection with the power system network.

Soil resistivity measurement is also required to design the ground grid before construction.

Step and touch potential is calculated and not field measurement is required.

Perhaps the enclose site will be helpful in this post

http://www.wapa.gov/rm/psmmCHAP-08.pdf

RE: step and touch potential

cuky2000

That was excellent posting and advise cuky.

RE: step and touch potential

2
I have some amount of experience with tingle voltages on plumbing and properly grounded appliances. In 1 case a 40 foot long or so underground conduit had rotted to the point where it was leaking 7 amps at 120 volts during a drought. The current flow was energizing the drainpipes and basement floor.

To get rid of the nasty tingle voltage at the bathtub I had to bond the cold water pipe, the hot water pipe, AND the drain pipe to the grounding electrode conductor. Since Article 680 of the National Electrical Code allows homemade ground clamps that are made out of stainless steel I used stainless steel hose clamps and washers to bond to the cast iron drain pipe. I also had to file a bare spot on the cast iron and then corrosion proof it with Ilsco Deox electrical grease. Some utilities require this when you have an electric water heater - good idea even if you do not have one.

To get rid of the tingle voltage at the washing machine I had to just simply cut the power to the detached garage.

If you are really worried about the resistance of your substation ground mat you should think about sinking some copper or galvanized steel pipes very deep into the ground. If your soil is amenable to it you can use a Borit or Borzit (2 different companies) directional drilling tool to sink the pipes into the ground. This is a rather cheap tool that is used for directional drilling underneath driveways and sidewalks and to build small diameter shallow wells. Plan on having to leave the drilling bit at the bottom of the hole. You could also drill small holes ( 1/4 inch 6 millimeter) holes along the pipe so that you can attach a water hose to the top to beef up soil conductivity. You may even be able to configure some as shallow wells for watering the others.

Or, have a well driller sink some metal well casings well below the water table. You could also do a combination system that uses deep wells to irrigate your ground mat.

Mike Cole, mc5w@earthlink.net

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources