high strength anchor bolts
I'm designing the foundations for a building. The bulding steel designer has specd A325 anchor bolts to be pretensioned. I believe he needed to do this because he has a case where the bolts need to resist overall uplift and a moment. Pretensioning the bolts I am assuming would preload the baseplate in compression so he could develop the tension to resist the moment.
1. Does this sound reasonable?
2. What pretension value is required for something like this?
3. Does the pretension value get added to the over all tension in the bolt to come up with the required bolt size?
thanks for any insight
RE: high strength anchor bolts
The effects of pretension are summarized in this link below. The information seems reasonable. It should help answer some questions about how pretensioned connections behave. I would expect one of the more senior members of the forum could give you a better answer than me, I hope my little bit helps some.
http://www.unified-eng.com/scitech/bolt/clamping.h...
There's also some good info on weld symbols in the menu to the left side of the above referrenced link.
Go to the AISC web site. In the "Steel Interchange" questions from September 2003, there was a discussion on pretensioning anchor rods.
In short, tension in anchor bolts is normal. As long as the nuts are tightened to prevent a dynamic action on the bolt, it should be sufficient to mobilize the resistance.
a. You had a clearance between the base plate and its bearing surface (concrete or grout) that is greater than the edge distance of the bolts (otherwise the compressive side of the couple is placed at the point of contact with the bearing surface)
b. The frame (and/or base plate) had so much flexibility that significant wracking could occur with large lateral deflections (we hope not, since most designs check for this)
If your bolts are even reasonably snug, this will not happen. Further, if you are concerned about such, put nuts above and below the base plate, then back-grout the space.
The premise your are proposing would only occur under very large movements of the column and base plate. This is not the case for most applications.