Switchgear temperature rise
Anyone any guidance on how to keep the temperature rise of an LV (400V) Switchgear cubicle below 60K (ambient 35 deg) for UK use. I need to know how to calculate current carrying capacity of copper and ensure that the cubicle has sufficient venting to keep temp down. Any advice would be well appreciated.
RE: Switchgear temperature rise
QUESTION: Anyone any guidance on how to keep the temperature rise of an LV (400V) Switchgear cubicle below 60K (ambient 35 deg) for UK use.
ANSWER: One way is monitoring the temperature providing alarm or switch to start the cooling system.
Check if the enclose monitoring device could work for you.
http://www.squared.com/us/services_support/squared...$file/WirelessTemperatureMonitoring.pdf
QUESTION: I need to know how to calculate current carrying capacity of copper and .......
ANSWER: For temperature rise calculation guidance, see standard DIN EN 60439-1 or other relevant standards. There is good information in section 4.4 of the ABB Switchgear Manual 10th edition.