How do you test fault ride through capability?

How do you test fault ride through capability?

How do you test fault ride through capability?

(OP)
Hi all,

I am in the situation where we are wanting to determine the fault ride through capability of our synchronous generator.  I know that these things can be modelled using the inertia of the generator, AVR charecteristics, etc. But how would you go about testing this in the field?

Do you have to simulate faults by shorting to earth through some variable impedence?  Or is it sufficient to just disconnect the generator and monitor the phase alignment?

Or is there another way?

Many thanks for any help.

RE: How do you test fault ride through capability?

What type of generator is this? Turbo-generator? Small diesel?

Besides normal protective relaying commissioning, one of the key items to test is the generator unloading behavior. When a fault occurs, the generator may be relieved of a significant portion of it's load. The speed control and AVR must respond quickly and appropriately. I couldn't recommend deliberately faulting the generator.

RE: How do you test fault ride through capability?

(OP)
The generator is a 670kVA generator designed for a diesel genset.

What is "normal protective relay commissioning"?

RE: How do you test fault ride through capability?

Protection functions on a generator this size might include overcurrent, over kW, reverse power, over/under voltage, over/under frequency, overspeed, overtemp, field overcurrent and loss of excitation.

Normal genset testing would include some or all of the above along with prime mover protection functions, steady state voltage and frequency performance at various loads, block load and unload performance, and sustained full load.

As you say, fault performance depends on the speed control, AVR, excitation system, prime mover and throttle actuator. The AVR may include field forcing to sustain output during faults.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources