Transmission Line Zero Phase Sequence Impedance

Transmission Line Zero Phase Sequence Impedance

Transmission Line Zero Phase Sequence Impedance

(OP)
In Australia there are large salt lakes. I am modelling a transmission line which runs on a low causeway built through the middle of one. Does any one have measured or calculated values of earth resistivity for such an environment. Values in Ohm metre are prefered.

RE: Transmission Line Zero Phase Sequence Impedance

The resistivity of sea water is approximately 20 ohm-cm.  This would definitely have an affect on the tower resistance regardless of the resistivity of the causeway soil.  It might be worthwhile to use grounding analysis software with the capability of modelling the causeway and salt lake as separate volumes.  The SES CDEGS package has this capability; see http://www.sestech.com

RE: Transmission Line Zero Phase Sequence Impedance

RE: Transmission Line Zero Phase Sequence Impedance

I just noticed the subject line.  You are after the zero-sequence impedance, not the footing resistance.  In this case, you need some average resistivity to use in Carson's formulas for re and xe.  The equivalent depth of return depends on the resistivity and the soil is assumed to be homogenous which it obviously is not a very good assumption in your case.  Fortunately, the line zero-sequence impedance is not all that sensitive to the resistivity.

For a typical 115 kV vertical construction Drake conductor line, I calculate the following zero-sequence impedances:

rho            R0         X0
(ohm-m)       (ohm/km)   (ohm/km)

0.01           0.250      1.189
0.1            0.257      1.441
1              0.272      1.690
10             0.294      1.935
100            0.323      2.178


Fault values are only partially dependent on the zero-sequence impedance, so this makes the overall result even less sensitive to resistivity.  If the entire line is on the causeway, you should probably assume something low if you are concerned mostly with maximum fault levels.  The current will not flow entirely in the salt water, so based on the graphs Cuky provided, I'd probably pick a resistivity of 1 ohm-m.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources