Ventilation - Intermittent Occupancy
I have a client installing a ventilation system in a movie theatre. The capacity is 400 people and from ASHRAE standard 62-1999 requires 15cfm/person equalling 6000cfm total.
My question is regarding the intermittent occupancy considerations (section 6.1.3.4 of the standard). This specifies that for peak occupancies occur for 3 hours or less, one half of the maximum ventilation (3000 cfm in this case) is permitted. What it doesn't specify however, is the period that the space must be unoccupied for this to be valid. In a movie theatre setting, yes there is intermittent occupancy, but sometimes probably for only 15-20 minutes at a time before the next group comes in.
Anyone have any experience dealing with a similar situation?
Thanks.
Thanks.
RE: Ventilation - Intermittent Occupancy
Also, what state are you in? ASHRAE 62 has a bunch of addednda that you might be required to use. One change is the way you figure out required ventilation air.
82% * 400 = 328 people on average
328 ppl * 15cfm/person = 4920 cfm required
I will also be using CO2 on demand sensors, as it will be rare the theatre will be at full capacity.