Is it ok to install 25kv URD cable in ladder tray
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: 25kv URD cable in tray
If you're a US utility, you can do whatever you want, without regard to NEC in substations and power plants.
Tray cable is tested for flame propagation and URD probably is not.
For NEC compliance it would also have to be isolated from any low voltage cable by a metal barrier.
RE: 25kv URD cable in tray
Is the cable sunlight (UV) resistance rated?
Even if the cable tray system meet code requirement, URD cable installed in tray may not be the most economical choice since the concentric neutral can be saved if the metallic cable trays is permitted to be used as Equipment grounding conductor (EGC) where continuous maintenance and supervision ensures that qualified persons will service the installed cable tray system as stated in NEC Section 318-3(c).
RE: 25kv URD cable in tray
Little bit off topic, but:
How do you insert such an image?
Is it a certain type of file, a certain method or just magic?
Thanks
Regards
Ralph
RE: 25kv URD cable in tray
This is an awesome tool to illustrate our point of view.
For image available in the web, use the [img] tag. The way to show this in the post is typing the following:
[img “internet address” ]
“Example of internet address” = http://www.matel.com.mx/gif/cablepic/e07.GIF
For additional details attaching images and other editing tips, access TGML tags list from the preview mode on the post window.
RE: 25kv URD cable in tray
It is in Canada
Need to carry neutral from main sub station to existing 25kv O/H ploe line. Because bldg is in the way, Cannot run O/H line all the way. So part of run is cable on top of roof.
Since hard to find 25kv 4C plus ground armour cable. Thinking to run URD in tray on top of roof.
Or any other suggestion
RE: 25kv URD cable in tray
Who owns the cable? IF it's a utility and the NEC does not apply. I have seen try use in large vaults ( approaching swimming pools in size ) to support red stripe cable.
RE: 25kv URD cable in tray
Maybe I have to replace my glasses...
Regards
Ralph
RE: 25kv URD cable in tray
It is not utility. I will be contractor supplied.
It is industrial plant.
Cannot run underground.
RE: 25kv URD cable in tray