Expansion joint in hig rise building
I'm working on a 35 storey twin tower with combined ground &parking floors (P1, P2 ,P3) in which expansion joints are located both in X & Y direction. At each expansion joints there is two columns 2 cm apart resting on pile foundation with pile cap.The pile cap is combined one for both the column. The problem is our client engineer insists for expansion joint must start from pile foundation itself . ie, seperate pile cap for each coulmn set apart 2 cm spacing at expansion joints. But design engineer says expansion joints starts from column only and no need to provide expansion joints in pile cap. Who is correct client engineer or design engineer? please comment and save me from this dilemma...
thanks a lot
regards
thanks a lot
regards
RE: Expansion joint in hig rise building
If you are in a seismic zone or an area heavy with frost action, expansion joints in the foundation will allow for lateral expansion. However if wind is the only consideration you probably don't need expansion joints in the foundation. This is especially true for tall structures. Generally, the largest deflections are at the top of a building and decrease as you go down toward the foundation. Therefore, expansion joints are more critical the higher you go as there is more movement. In other words, the foundation will not sway in the wind like the top of the building will, so expansion joints in the foundation are a good idea but not necessary based only on wind forces.
Expansions joints are added to offset the effects of thermal movements in the building. For foundations, the temperature range is very small, if not zero, so the thermal movements aren't there. For a very large footprint building, yes, you might consider separating the foundation areas with joints as there could be build-up in stresses in gradewalls, etc., due to foundation settlements or heaving. But generally, the expansion joints start at the base of the building columns and walls.
hi haynewp
The project is in Dubai UAE. So out of seismic area. Here the temperature variation is very high (Average temperature 40 C and max 50 C).Up to the parking floor expansion joints is in both direction X & Y, after that only in Y direction.