sizing of transformer
sizing of transformer
(OP)
I have 9 110V ac to 5kv transformers, these are energised for 1 second periods every 60 seconds. I also have 3 110Vac panel mount octal type relays powered on continuously.
How do I size the transformer required to step down the supply from 230 to 110, & size the fuse required.
Thanks
How do I size the transformer required to step down the supply from 230 to 110, & size the fuse required.
Thanks





RE: sizing of transformer
Each 5kv transformer primary should be fused. Use a fuse rated for the continous primary current of the 5kv transformer. This will protect the transformer. If it is necessary to protect the load, more information is required.
Use one fuse for the three relays. Fuse the relays for 3 or 4 times the current the relays actually draw.
The preceding is based on the assumption that the 5kv transformers are small since they have a 110 volt primary. Thus it will cost less to oversize the stepdown transformer rather than having an optimum design.
Also if it is likely that the 5kv load will have frequent short circuits, use circuit breakers rather than fuses.
5kv IS DEADLY. HAVE A QUALIFIED PERSON REVIEW YOUR DESIGN.
RE: sizing of transformer
Mike Cole, mc5w@earthlink.net