Modified Sine Wave

Modified Sine Wave

Modified Sine Wave

(OP)
Does anyone have experience running a motor on a modified sine wave? I have a motor on a valve actuator that I would like to run off of an invertor which outputs a modified sine wave, the output is more or less a square wave with some dwell on 0V, like below. I just want to know if anyone has experienced problems doing this. The invertor company says it should be fine, but I'd like to hear from the experts.

 __        __       __
|  |_    _|  |_   _|  |
     |__|      |__|

RE: Modified Sine Wave

It should not be a problem. Running a drive motor continously could (perhaps) lead to more heat because of the harmonics in the waveform. But a valve actuator usually only runs for short periods and the extra heating should not be a problem - unless, of course, that the valve opens/closes continously. In the latter case, I would have a look at the valve controller and try to stabilise it.

RE: Modified Sine Wave

(OP)
Thanks, that's exactly what I thought. The motor only runs for about 82 seconds to close the valve and happens only once a month or less so it should definately not be a problem.

RE: Modified Sine Wave

This used to be the standard for Variable Frequency Drives (6-step inverters), but causes some long term problems that can be avioded with more modern PWM style drives, so the design has fallen out of favor. However, as skogsgura said, for a short duty cycle application like this it should be just fine, and they tend to be very rugged and reliable, desireable qualities in valve actuaters if you ask me.

"Venditori de oleum-vipera non vigere excordis populi"


RE: Modified Sine Wave

The signal you are generating is a PAM (pulse amplitude modulation) singal. These types of signals are still commonly used in oil and water wells due to the length of the cable. Granted, most are now 12 pulse or 18 pulse type signals.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources