How much leakage should be speciffied for a Rubber Gasketed
Reinforced Concrete Pipe, class B-25 , ASTM C361?
There are any standards regarding maximum laekage allowance for this kind of pipe?
Can the pipeline meet 20 gals/24 hrs/inch dia/mile?
Thanks
Reinforced Concrete Pipe, class B-25 , ASTM C361?
There are any standards regarding maximum laekage allowance for this kind of pipe?
Can the pipeline meet 20 gals/24 hrs/inch dia/mile?
Thanks





RE: Leakage test for RGRCP
Diam of sewer (inches) Infiltration per ft. per hr. (Gal)
4 0.0063
6 0.0095
8 0.0126
10 0.0158
12 0.0190
15 0.0237
18 0.0284
21 0.0332
24 0.0378
27 0.0426
30 0.0474
36 0.0568
42 0.0663
48 0.0758
42"diam Manhole- 0.0663 Gal per vertical ft. per hr.
48"diam Manhole- 0.0758 Gal per vertical ft. per hr.
Perhaps your State has similar limits.
MIKOLAY