Hello,

I trying to determine the maximum length that thermocouple (extension) wire can be run from the connection head directly to a PLC T/C board. Is there a standard (API, ISA, IEEE, etc.) which addresses this installation question?


Best,

KC

RE: Max Recommended Distance That Thermocouple Wire Can Be Run

depends on the input impedence of you a/d and the size of you extension wires. At one time runs of several hundreds of meters were common in large plants. These days it is a toss-up as to the cost of a transmitter at some satellite point versus the use of extension wires. with the plc you have to confront CMRR and CMR voltagesif you are using grounded sensors and using exceptional run distances.

it is a engineering not a standards item although some customers may have recommended practices that you have to comply with.

RE: Max Recommended Distance That Thermocouple Wire Can Be Run

I used to work at a very ancient plant as an Instrument Tech back in 80's and T/C wires upto 500 yards were very common there (both "K" and "J" type).

RE: Max Recommended Distance That Thermocouple Wire Can Be Run

Both are right.  I used compensation cable of 500 meters at the past.  Nowadays we prefer to install a 4-20 ma transmitter at the Therocouple and run the 4-20ma signal to the PLC.  I had problems with direct connecting  TC  to the PLC and using RTD (PT100) for direct connection or using transmitters for long wires.  Transmitters are at the 80 to 120$ range, and you can get good transmitters from Mescon (www.Mescon.com),  RP Electronics (www.RPElectronics.dk), Minco (Minco.com) and others.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources