Uninterruptible Power Supply (UPS)
Does anyone know of any UPS manufacturer that provides a UPS with the following characteristics:
1- Input: 120/208V, 3PH
2- Output: 120/208V, 3PH
3- Capacity: 30KVA
4- Battery: 1 to 2 hours backup time without need for external battery pack
5- Power Factor: 1 or very close
6- Harmonics: Good THD<=3%
7- Good Crest and Surge factor
Thanks in advance for your help
3- Capacity: 30KVA
RE: Uninterruptible Power Supply (UPS)
TTFN
For this spec, your battery will probably weigh somewhere around 1500 to 3000lb.
there is no such thing as internal battery for 30kVA UPS units and specially for 1 hr.
You need to decide, which one you want, so called 'internal battery' (not requiring additional cabinet?) or 1 hr back up. Can't have both.
"Venditori de oleum-vipera non vigere excordis populi"
30kVA is at the bottom end of the GEDE size range, but the technology is common across the range. As with everything, you get what you pay for, but by dealing direct with GEDE in the UK we paid a fair price for a good product.
If we learn from our mistakes,
I'm getting a great education!
Mike
It could get you in trouble if the UPS is fully loaded. In most cases I see around 0.9 lag aggregate.