Motor direction for VFD powered motor

Motor direction for VFD powered motor

Motor direction for VFD powered motor

(OP)
Hi all:

I have a piece of equipment with two (2) 480 VAC 3-phase motors on it.  One of these motors is controlled by a VFD, the other is branched directly from the main feeder.  When my customer has the equipment located in Room "A" both motors rotate in the correct direction.  When the equipment is moved into Room "B" the motor connected to the VFD continues to rotate correctly, but the other motor rotates in the opposite direction.

Is it true that that phase order of the conductors feeding the VFD will have no effect on the connected motor's rotation?  In other words, switching two of the conductors feeding the VFD will not reverse the direction of the motor, the conductors must be switched either at the motor junction box or on the output side of the drive.

The search function doesn't seem to be working, so I apologize for this simple question which has probably been answered before.

RE: Motor direction for VFD powered motor


You are correct about the VFD.....

They convert the 3-phase input to a DC voltage before 'chopping' it back to 3-phase again at the required voltage & frequency.......

RE: Motor direction for VFD powered motor

But if the motor leads (output of VFD) are transposed..it will reverse the direction...

RE: Motor direction for VFD powered motor

Yes, The AC power into the VFD is rectified and then converted to controlled three-phase AC.For that reason the motor driven by the VFD does not changed rotation.

It seems that the phase sequence of room B is reverse as compared to room A.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources