Can you help me ? Durable concrete test required slump test and air content test ?
I see the slump test in ACI-336.1-01
But I don't know much about air content test , purpose and range of air percent and what ASTM or ACI spec use for it .

Thanks you

RE: Air content test

For determination of air content in plastic concrete, we normally use ASTM C231 as test procedure.  If you have light weight aggregates, you may have to use ASTM C173 test procedure.  

Air content is very important for durability in freeze-thaw environments.  Specs are commonly location and job specific.  We commonly see air (where required) as low as 4% and as high as 8%.  ACI, CSA, AASHTO,and other authorities etc. will provide guidance as to suggested air content ranges for various applications.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources