Max. Air Change Rates for Animal Hospital!!!

Max. Air Change Rates for Animal Hospital!!!

Max. Air Change Rates for Animal Hospital!!!

(OP)
Guys,

I have some Misc. rooms in an animal hospital that were questioned by my boss if we need the amount of air changes/hr that the GC requested.  Currently we have an animal ward room that was requested to have 8.5 ac/hr......x-ray & surgery rms @ 7.1 ac/hr...etc.

Does the International Mech. Code or Energy Code cover max. allowable air changes for specified rooms??  

I've looked, but can't seem to find anything.

Can anyone help??

RE: Max. Air Change Rates for Animal Hospital!!!

In the United States the” Guide for the Care and Use of Laboratory Animals," is typically used.  Ventilation design 10 to 15 air changes per hour for most facilities.  

Also, some criteria is in ASHRAE's Applications Handbook.

RE: Max. Air Change Rates for Animal Hospital!!!

(OP)
Thanks guys,

Your input was a big help..one other question pops up to me now though.  Is the recommended Air Change rate based on the total space load, or is it just based on ventilation?

RE: Max. Air Change Rates for Animal Hospital!!!

You would have to check the load. If the load calcs require larger ACPH, then provide it. The 15 ACPH is the minimum to control odor. Beyond it there is minimal odor reduction. with larger ACPH. Pharmaceutical companies typicall use 20 ACPH in non clean room manufacturing spaces.

RE: Max. Air Change Rates for Animal Hospital!!!

Does anyone (in the USA) know what codes, regulations, or accepted guidelines I need to look at for welding exhaust in a school welding shop?  I've tried IMC, nothing specific there.  How about OSHA?  

A Mfr wants to sell me a portable recirculating unit with a 95% efficient filter instead of the specified exhaust arm tied to an exhaust fan.  Does anyone have specifics on whether or not the air can be recirculated?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources