I have a current imbalance in a three phase chiller motor (480v 300 hp)Each phase: 1- 200 2 - 215 3 - 252. The voltage imbalance for this is less than three percent. We are also seeing other motors in the facility experiencing current imbalance. We also see the power factor readings for each leg can be more than 1o percent diffeent. If one motor suffered current imbalance I would suspect a motor problem but five tend to lead to a distribution problem. Is it possible several nonlinear loads (277 lighting, etc.) can be a contributing factor?
Run1on
Run1on





RE: Current imbalance in three phase chiller motor
RE: Current imbalance in three phase chiller motor
The customer has lost their contactors once already. I will schedule a meeting with the local utility and request they meter their incoming supply for minimal requirements. This customer is at the end of the line and I suspect the KVAR generation of the utility is not sufficient to support their needs. As such we may have to install the necessary KVAR correction.
Run1on
RE: Current imbalance in three phase chiller motor
RE: Current imbalance in three phase chiller motor
RE: Current imbalance in three phase chiller motor
I would point out that it is not the "nonlinear" nature of the loads that cause an unbalance problem, but rather the fact that single-phase loads (like the 277v you mention) may not be properly balanced among the three phases.
I'm not sure that capacitive support is necessarily the solution to unbalanced voltage. It'll help raise the overall voltage... but I don't think it'll reduce the unbalance. The way I look at it you either need balanced single phased loads or else a lower impedance path from the source (possible add parallel lines) which would reduce the effect of a given imbalance.
RE: Current imbalance in three phase chiller motor
RE: Current imbalance in three phase chiller motor
The chiller's current draw is not consistent some of which can be due to load demands and possibly due to a load limiting functioning programmed into the unit . The unit is drawing nowhere near the FLA high end of 400 amps between 200 and 270 is normal.
I want to thank everyone who has responded. It was a exciting moment to find a site where I can receive help from fellow engineers.
Kevin
Run1on
RE: Current imbalance in three phase chiller motor
You find that your chiller FLA readings will continue to raise and lower. Check to see what the purge count on the chiller is. It only takes a few purges to knock your vanes out of calibration. This will cause a chiller to "run all over the place" trying to find a set point that satisfies the load condition. This will be especially apparent during low load conditions. I would have the service provider/chiller manufacturer return to re-calibrate the chillers. Is your chilled water temperature remaining stable? Are sufficiently removing humidity from the classrooms? Have ever experinced any flow problems with either chilled water or condensed water?
RE: Current imbalance in three phase chiller motor
As regards a coordination study, I am at a loss to understand what this would have to do with correcting the unbalance situation. I believe that a power quality study may be in order to identify problem areas and to determine corrective action.
What is the overall power factor, supply transfomer rating, load and measured voltage level within the plant? This info would be a starting point to evaluating the need for/benefit of capacitor addition
RE: Current imbalance in three phase chiller motor
RE: Current imbalance in three phase chiller motor
‘the utility’ and a 300hp, 480V motor.
In the simplest sense, voltage is source based (the utility) and current is load based (the school/chiller). Without basic but systematic measurements and comparison to labeled ratings it is hard to draw reasonable conclusions.
At this point, consider the skilled use of a basic power analyzer–something that can look at waveforms, and not just the raw voltage and current quantities from a multimeter. A “walk around” by a person familiar with the site (and in possession of system drawings) and someone who is experienced in identifying the effects of electrical interactions can be time and money well spent. Because of the potential cost of chiller electrical damage, you may want to consider retaining–or at least consulting with–an electrical engineering firm or service to interpret the measurements if they’re not well understood by the immediate user. The technical person or firm should be able to identify the problem and prepare a report whose information will ultimately influence the possibly non-technical administrator that has budgetary authority. If the problem is allowed to persist and failure(s) occur, you can bet the administrator and his superiors are going to be asking some embarrassing questions about how their maintenance funds have been spent.
RE: Current imbalance in three phase chiller motor
The only time you could actually reduce the imbalance is if you had unbalanced system voltages (even with motor secured) AND unbalanced-impedance motor. Is that the situation you're referring to?
RE: Current imbalance in three phase chiller motor
i.e. 1- 245, 2-275, 3- 278. The corresponding current readings for this time frame are:
1- 2 , 2- 66, 3-510. We see this throughout the entire data record which is two days long sampled at one minute intervals at every startup occurance. We are in the process of taking readings on the ground to see if a partial fault or phase to ground event is occuring.
RE: Current imbalance in three phase chiller motor
Thanks
RE: Current imbalance in three phase chiller motor
Some more discussion on dividing the problem into motor or supply (and by supply I mean in-plant plus utility):
Normally the observation that the location of high current stayed with supply phase vs motor phase during lead swap would lead you to suspect the supply, not the motor.
Normally the observation that the voltage was balanced without the chiller running would lead you to suspect the motor, not the supply.
You mentioned current imbalances on other motors also, tends to point toward the supply since it's not likely all motors have a similar problem.
Put the above together and you start to suspect that it is a supply-based problem which only shows up when you put a motor load on it. perhaps a high impedance on one phase of the supply circuit which doesn't show up until you put a load on it.
But there's another piece - the currents you reported
"1- 2 , 2- 66, 3-510". Obvsiously a HUGE imbalance. (When did it changve from 1- 200 2 - 215 3 - 252 as originally reported?). In fact there is not enough current within phases 1 and 2 to provide return path for current from phase 3. So you have to suspect an alternate return path through a ground.
But if the ground were within the motor, then your swapping lead trick would have left the high current at the same motor lead. UNLESS - the location of the ground was upstream of where you swapped the leads but downstream of where the motor is normally switched on/off. Assuming you swapped leads at motor terminal box, this could be anywhere between the load side of your starter and your terminal box.
Getting a little far into the speculation stage. If there is a ground it shouldn't be hard to find. Start by meggering from motor with all leads attached. If ground detected, then disconnect leads and see which side it's on.
Let us know if you get more info.
RE: Current imbalance in three phase chiller motor
RE: Current imbalance in three phase chiller motor
You’re better off building an air-tight case before extending any blame. Careful measurements and documentation are vital for resolving the problem.
From a purely mechanical aspect, did the chiller seem to be operating acceptably? With the listed current readings, the rotor would likely be stalled. Have [chiller] readings been verified as correct at the motor terminals with known accurate instruments? The wide range of current readings are suspect, but you know the history of the system better than others here. Remember that, for utility equipment to be involved, the readings must be reflected at the service entrance; i.e., where the utility and customer’s facilities meet.
(For the sake of other readers, phase rolling to match service conditions is discussed in §11 at: http://www.pge.com/002_biz_svc/pdf/058087g.pdf but my understanding is that the process is intended for a one-motor / one-transformer arrangement.)
RE: Current imbalance in three phase chiller motor
1. Voltage imbalance is often related to load imbalance on multi-phase supply systems.
2. Traditionally, first attempt to rectify the problem was to use clamp-on ammeter and measure currents at panel's feeders to find out the load imbalance. If the load imbalance is spotted some one or two-phase circuits, causing the load imbalance and potentially the voltage imbalance, have to be switched to different phases. This may need several tries since the certain loads may or may not be on, but it is worth it. The three phase loads are usually fairly balanced. If they are not, they are experiencing some internal malfunction, either open circuit nature or short circuit nature. This procedure is widely used and yields reasonable results. It is a good idea to record reading and perhaps input it in a good spreadsheet without bugs for quick updates.
RE: Current imbalance in three phase chiller motor
1) The chiller runs reasonably well after startup; it has a problem with cycling that needs to be addressed by the manufacturer.
2) We just finished checking other feeders from the MDP and found current imbalance on almost every breaker in the panel.
3) We turned the chiller off at the MDP and the current imbalance was still present in other feeders
4) There was only 2-4 amps to ground and various neutrals showed minor amperage.
5) the feeders from the utility transformer showed only a 1 volt deviation among the phases buring both chiller operation and stoppage. They have said they will help set up monitoring of the transformer and are providing paperwork from tests done previously. They state they are in ANSI compliance.
6) We have decided to take the approach noted by jbartos and examine every panel for current imbalance and adjust as necessary. It is possible since there was a major renovation at this school, the engineering firm may not have done an adequate job of load balancing between new and old circuitry. Will find out.
Thanks everybody
RE: Current imbalance in three phase chiller motor
One approach to finding the problem, in addition to those noted in the excellent posts above, would be to find where the voltage imbalance starts.
With the system loaded, begin at the line side of the main breaker and move to the load side, then further downstream until the voltage unbalance is found. When you get to this point, the element immediately upstream will be the culprit and appropriate corrective action can be taken. Offline tests to confirm the condition would include joint & contact resistance checks, using a Ducter or high current source (NOT an ohmmeter).
RE: Current imbalance in three phase chiller motor
I find that conclusion highly plausible. This school renovation was repeated at two other schools with the same design firm and electrical contractor. It is very possible When I have the results of the further investigations I'll post them. It helps greatly when a question is posed and the result is given to everyone.
We found a discolored phase wire on a subfeeder this morning; this feeder fed the kitchen area and we're waiting for the load usage to go up in the area to IR camera the joint to see if it is loose.
Thanks
Run1on
RE: Current imbalance in three phase chiller motor
With the discussed imbalances, you may be able to smell the joint failure. Depending on how much overtime you need, consider in-service, energized millivolt-drop tests on the electrical-gear busbar joints, breaker/fuse poles and„Ÿcarefully applied„Ÿcable terminations. Use a power-rated multimeter set on the AC-millivolt range, that will not be affected (except for an overrange reading) if unintentionally applied at any phase-to-phase voltage. Load currents must be roughly at their usual for the readings to have meaning. There is the advantage of have three times everything (one per phase) for comparison. A low-end infrared thermometer or multimeter accessory would be helpful, too.
RE: Current imbalance in three phase chiller motor
I hadn't thought of the on line millivolt drop test, but it sounds like a great idea. Just a word of warning to the unwary - only try this if you are fully conversant with all safety implications, as it entails working on energized circuits, possibly defeating door interlocks etc.
Yes, the infrared approach can be a winner here as well - it probably is the easiest test to do under the circumstances.