DISCONNECT OR NOT

DISCONNECT OR NOT

DISCONNECT OR NOT

(OP)
We have (1) 10HP, 575 Volts 3p motor and
             (2) 70kW, 600 Volts 3p heater
provided to be connected to one circuit from 600V A.C. panel.
Each load ( heater or motor)is delivered with its own fuse protection.
Is it necessary to provide diconnect (or fuse switch)between these fuses and main C.B.
I mean two disconnects - one for heater plus one for motor.
I am in Canada
Thanks.

RE: DISCONNECT OR NOT

I would say as long as your equipment has a disconnect on it, you should be fine (preferrably lockable).

Mike

RE: DISCONNECT OR NOT

Where is the motor overload protection relay?  If it is located at the main CB(which feeds to both motor and heater), I don't think it is a correct location.
If you don't have overload relay but you can afford to have the motor burnt-out when it gets overloaded, then it is not a concern.

The question of disconnect switches for motor and heater depends on whether you need to isolate only one of the two.  If you always have to shutdown both of them, the main CB (padlockable) should be sufficient.

RE: DISCONNECT OR NOT

What is the application? This sounds like a AC unit with a reheat coil? Is this an assembly??

RE: DISCONNECT OR NOT

Section 28-600 of the Canadian Electrical Code covers disconnecting means for motors.  Take a read.
I think that 28-604 (3) applies and you need a disconnect within sight and 3 meters of the equipment.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources