Finding LRC from NEMA MG 1 "Code Letter"
How do I determine the locked rotor current of a motor if I know the Code Letter from the nameplate? The motor is a 460V, 10 HP motor with code letter "H".
RE: Finding LRC from NEMA MG 1 "Code Letter"
Maybe I'm wrong, but that 'H' is the insulation class is it not? I would think the full load amps (FLA) rating would be quite close, if not exactly what you need. I have no idea what your motor is, but I looked at 3 misc. 10HP 460V motors and the FLA's range from 12.3 to 13.8A at 460V.
From here, I am lost or missing something. The motor is 460V with a PF of 76%. I think this should leave me with a LRC of 136A, but that is much higher than the manufacturer specified (80A LRC). Where did I goof up?
Gherian, might you mean 63kVA locked-rotor? {63,000 voltamperes} A range would be 63-71kVA for code-H / 10 horsepower.
So for 10 hp motor, maximum would be 70.9 kVA. At 460V, this is about 89 amps. This is a symmetrical rms value. The asymmetrical current could be a lot higher than this. On the other hand, if you have a lot of voltage drop, the current will be less.
This assumes a full-voltage start, of course.
The "code leter" gives a range of starting kVA per each HP.
As you mentioned H corresponds to 6.30 to 7.09
So the starting current will be:
Imin = 6.3*10(HP)*1000/(1.732*460)= 79.074 Amperes
Imax = 7.09*10*1000/(1.732*460) = 88.89 Amperes
Note that here the PF is not a factor since you are interested in the total power, active and reactive.
The manufacturer gave 80 amperes which comply with the standard.
The Code letter is an indicator of starting inrush while the Insulation Class is mostly a measure of insulation temperature tolerance.
Both can have an H marking on the nameplate but it means something completely different depending on where it is.