Modicon PLC 984-A145 & Stop code 0010H

Modicon PLC 984-A145 & Stop code 0010H

Modicon PLC 984-A145 & Stop code 0010H

(OP)
I've just downloaded a program to a modicon CPU , model 984-A145.
Now the CPU won't go into RUN. help..

Modsoft programming software giving STOP CODE 0010H and the PLC status tool indicates an IOP failure.
ie status word 5, bit 12 is high.

What does IOP failure mean ?
Is it a software or hardware error ?
Any help would be appreciated

jb

RE: Modicon PLC 984-A145 & Stop code 0010H

Look very closely at the network number that is displayed during the down load process. This number changes as the program is being compiled net by net. The network number that is displayed when the error occurs is the network number where an error has occured in your program. The code you wrote has an error.

best regards, PLCSAVVY

RE: Modicon PLC 984-A145 & Stop code 0010H

i have a program that has been in use for 7 years that went down with a 0200H error, and when repowered and tried to restart, gave the 0010H error as a reason for not starting. is there a specific error in code that causes this? because this is an existing, tested and working program tghat came up with the same issue.

RE: Modicon PLC 984-A145 & Stop code 0010H

The 00002 error is a corrupt memory error. Possible sometimes to power up restart. If not, attempt a reload. If that doesn't work then there is a hard failure. The 0010 error is a configuration/traffic cop failure. Also may be caused by corrupt memory or hard failure. On some models with a separate remote I/O processor (not the A145), if the program utilizes the remote processor and it is either not plugged in to the rack or failed, you will also get a 00010 error.

Bob
www.deltaautomation.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources