My client's existing 6kV system had consisted of 110/6kV main transformers (Primary side(110kV)-grounded wye / Secondary side(6kV)-delta winding) and Petersen coil to their 6kV system.

In this regards, I think there may be very few grounding fault currents when ground fault currents occurred on the existing 6kV system, and new 6kV switchgear 1,000 meters far from the existing 6kV system will be conneted through cables. My protection schemes for new 6kV switchgear are to use by combination of 67G (directional ground overcurrent relay) via ZCT and 64 (ground overvoltage relay) via grounding potential transformer (GPT) because I don't think that ground fault protection can be done by use of overcurrent ground fault rely (50G/51G).

I do not consider to use 67G for incoming CBs at new 6kV switchgear because it will be protected by upstream switchgear.

Do you have any idea for further consideration to properly protect new 6kV switchgear against ground faults?

Thank you very much for you kind advice in advance

RE: Ground Fault Protection for the Petersen Coil Applied 6kV System

Contact Areva (Alstom).

They have some MiCOM protection relays suitable for use on Petersen Coil Earthed networks.

Their website is www.areva-td.com

RE: Ground Fault Protection for the Petersen Coil Applied 6kV System

I have heard of use of Peterson's on the neutral of a 4WY, but how are they utilized on a 3WD?

RE: Ground Fault Protection for the Petersen Coil Applied 6kV System

(OP)
I understand your comments, please note that my client uses Peterse coils through zig-zag transformer connected to main bus. I think it is very unusual case.
Finally, I decided that 64 & 67G relays will be suitable for protection against ground fault on 6kV system.
Do you have any comments or advice?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources