Preventing sticking of AC/DC air solenoid valves after sitting idle
2

Preventing sticking of AC/DC air solenoid valves after sitting idle

Preventing sticking of AC/DC air solenoid valves after sitting idle

(OP)
In my assembly application - conveyor as well as stand-alone automated equipment, Numatics AC/DC solenoid valves are used to feed air cylinders to produce motion in lifts, tooling, and slide mechanisms.

After 1-2 days of downtime, manual actuation of many of these valves is required to "loosen up" the spool enough for electrical operation.

Is there anything we can do to prevent this nuisance - better air filtering, different lubricant, upgraded solenoids, etc.?

RE: Preventing sticking of AC/DC air solenoid valves after sitting idle

I have worked for 2 major pneumatics companies - see if your air line supply has a lubricator. There are two main types, Oil Mist and Oil Fog. Fog travels further down the lines. Check the distance from the lubricator to the valves against the manufacturer's specs, make sure you consider bends etc.

Lubrication helps with the valve operation and a small role in the solenoid, but you need to check if it is the Valve spool or the core of the solenoid that is sticking.

Remember - if you are using a lubricator on valves, then you MUST continue to use lubrication, as the oil spray will knock out the grease on valve spools. If your lubricator has run out of oil (Shell Tellus 32 works well) you may be running dry valve spools.

If your system is plc controlled - I'm sure you can edit the logic to run a test cycle every couple of hours while production is down. (just a suggestion!)

Solenoids do not vary too much, but valves do, Glandless (no rubber seals between the spool and the body) last the longest (millions of cycles), however most pneumatics manufacturers use the same solenoid assemblys to fire them. (ie. the solenoid is usually expected to last as long as the valve)

Dry clean air is a must!
Happy hunting


RE: Preventing sticking of AC/DC air solenoid valves after sitting idle

We use Numatics valves in our equipment and never have a sticking problem I know of.  Since our machines also have air bearings, we use clean, dry air; really clean and really dry.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources