can use steel beams instead of rebar for my reinforcement ?
I would like to know if I can use steel beams instead of rebar for my reinforcement in my concrete footing.
I have a 15'x15'x19" footing and since I have compressive and uplift forces I need to doubly reinforce my footing (top and bottom). However, based on my calculations I need a lot of rebar. I want to know if I replace the rebar with steel beams (that are connected by angles welded to them or running thru them) if I can accomodate for the area of steel required.
Any references, suggestions, or comments are welcome. Thank you.
RE: can use steel beams instead of rebar for my reinforcement ?
To answer your question, yes, as Slideruleera stated, it is acceptable.
If it is a structural slab (supported by piles, for example), 19" is not bad. The slab with normorl reinforcement rebars should take quite heavy loads. If it is a footing slab on soil with pedestals, the 19" may not be enough for the upward pressure. But in any case, conventional reinforcing should be considered first.
Try with increased depth, which is a economical solution.
My footing depth is not really limited other then I don't want to go too high. My footing is above ground on top of limestone. I have a pedestal that is 3'x3'x18" (my base plate is 2.5'x2.5'.) Which makes it already 3' above the ground including the 19" from the footing (15'x15'x19"). I ran different scenarios and I also get a deisgn of 15'x15'x17" for the footing and 3'x3'x12" for the pedestal.
My allowable soil bearing is 2500psf. My column loading is a compressive load of 280K, an uplift load of 167K and horizontal load of -55K (N-S)and 89k (E-W). I ran my numbers thru Enercalc 5.8 and StruCalc 6.0 both gave me very similar results and required areas for reinforcement.
I know since I have uplift forces I need to be reinforced top and bottom. The cost of rebar exceeds the cost of the concrete currently.
Am I going about the footing design incorrectly by using the same program for designing a footing above ground?
The required factors of safety that you actually need may be different, of course, because it depends upon the governing code that you are working under.
Let me run this by you to make sure I understood correctly:
I would need a total of 200k of concrete with a F.S. of 1.5.
[1.5 X 167K = (50K + Xk); where X = concrete weight]
So, based on that, if I were in the ground (vs being ontop)I would in addition add the weight of the soil acting on the fotting to counteract the uplift to make my concrete requirement smaller?
[Where 1.5 X 167k = (50k + Xk + Yk); where X = concrete weight, Y = weight of soil acting on footing]
First, recheck your shear calculations - you footing thickness is inadequate.
Second, solve your uplift problem by increasing your footing thickness and/or mobilizing adjacent foundation dead loads. As a last resort, you can use rock or soil anchors to resist the net uplift.
Third, now that your uplift problem is solved, you only need bottom reinforcement in the footing. If you've adequately sized the footing thickness for shear, the bottom steel should not be significant.
Good luck!
The limestone is a packed about 9" on top of the soil.
The plan is for the footing to be on top of the limestone to avoid digging into the limestone.
You can offset the uplift with drilled and underreamed piers. This is a lot easier than the approach you seem to be taking -
Please see FAQ731-376 for great suggestions on how to make the best use of Eng-Tips Fora. See FAQ158-922 for recommendations regarding the question, "How Do You Evaluate Fill Settlement Beneath Structures?"