very high chilled water flow effect.
very high chilled water flow effect.
(OP)
will increasing the flow in ahu's coil for (say 300% the design value) decreases the heat transfer from the air to the water?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
very high chilled water flow effect.
|
RE: very high chilled water flow effect.
RE: very high chilled water flow effect.
Other factors come into play as well, such as exceeding acceptable pressure drop across the coil, piping, valves, etc, which will probably show up as nasty erosion problems, as suggested by cub3bead.
RE: very high chilled water flow effect.
Thus, when applying the formula for heat, Q = UA.ΔT
you may notice that practically nothing changes when circulating more water than designed for.